Calibrating charge float voltage on Smart-UPSs

List of Smart-UPS models that have been confirmed to be able to have their float voltage adjusted using these instructions, and the number of reports:
  • SUA750XLI (1) (2003 vintage) (Reported by Wim, 07Dec2017)
  • SUA750I (1) (2009 vintage) (Reported by Wim, 07Dec2017)
  • SUA1000 (1)
  • SUA1000XL (firmware 631.3.D) (1)
  • SUA1500 (2)
  • SU2200 (1)
Units that respond to these instructions, but do not actually adjust the float voltage:
  • BP650S (1)
  • SU700 (1)
  • SU700NET (1)
  • SU1000XLNET (firmware 61.9.D, PCB 640-0732H, reported 18Feb2021 ALS)
  • SU1400 with firmware 70.9.I (reported by Marc van Dongen, 29Jun2012)
Contact me at asavage@iname.com to add models to this list.

Because I'm certain to forget this info, I write myself notes like this.

Problem: APC UPSs sometimes have a float charge voltage that is too high and tends to cook batteries. Here's a pair of gel/AGM batteries from a SUA1000 (not an XL) that have swollen so badly that I had to disassemble the case and pry the batteries out of the metal cage:


(click on any image for larger)
Image Image Image
Image

In the past, I've used multiple Costco FLA (Flooded Lead Acid) batteries to power my UPSs, and over the years I've learned to carefully monitor the water levels, because various UPS' charging circuits overcharge and keep the electrolyte gassing.

I stumbled across one post by Jacob Joseph that gave some clues to programatically changing the float charge voltage on some APC Smart-UPS models. Jacob indicated that he could change software parameters to change the float charge voltage on his SUA1500RM2, but not his SUA700, and he gives specifics. He goes on to relate how to modify the circuit physically on a Smart-UPS 1000, when a programmatic solution doesn't work.

At first, I was not able to make Jacob's software recipe work: I could not achieve SM (Smart Mode) mode, due to a missing step in his instructions. Later, in the APC Support Forums, I came across a reference to using <Shift+Y> as a trigger to put the UPS into Smart Mode, and then found this post that agreed. My missing first step: start with Capital Y.

But, while I could get my SUA1000XL into Smart Mode, I couldn't get it into PROG mode.

Then I found a reference in a third place that any & all SmartSlot cards must be removed before beginning, and Voila!

Note that APC has many different firmware revisions for their Smart-UPSs (as opposed to the firmware in the SmartSlot devices!), and the features available in Smart Mode vary. My SUA1000XL has firmware Rev. 631.3.D
  • Remove any SmartSlot card from the UPS. This might be a Network Management Card such as a AP9606, AP9617, AP9618, AP9619, or an Environmental Monitoring (EM) card. Just removing the two retaining screws and pulling it out of the chassis 1" is sufficient to disconnect it. While the official APC recommendation is to "Brain Dead" the unit before removing or installing SmartSlot cards, many people routinely change them hot (with the UPS ON), and that's what I do.
  • Use the Serial port. Because the SmartSlot cards must be removed, no networking is available, so you have to use the serial connection (or, perhaps, the USB connection if your Smart-UPS has one, but I haven't tried that).

    Connect the Smart-UPS serial cable to the UPS & PC (or terminal emulator, or, I suppose, a real terminal if you have one ;) ). In my case, the Smart Signalling 940-0024C (black) DB9xDB9 serial cable. No, you can't use a straight-through or null-modem cable. Other cables reported to be electrically compatible include:
    • 940-0024A
    • 940-0024B
    • 940-0024C
    • 940-0024D
    • 940-1524 (15')
    Note that APC has a lot of different cables for their UPSs, and few of them interchange as above.
  • Disable COM-port apps. If using PowerChute, or another UPS Service, disable it. The terminal program must have exclusive control of the COM port. Figure out which port you're using, if there's more than one. I've read at least one report that a USB<->Serial converter does not work for this procedure, but then a lot of USB<->RS-232 devices are buggy. [260120: I successfully used a Tripp-Lite Keyspan USA-19HS USB<->Serial adapter on Win8.1 to change the float voltage on a SUA1500]
  • Use a terminal program, such as HyperTerminal that's bundled with versions of Windows. Setup parameters are 8-N-1 (Google what that means, if you haven't used a terminal program before. HyperTerminal is not a very good terminal program, but it will suffice.). Flow control is variously recommended to be "None" or "Xon/Xoff". I was successful with "None", so I didn't try "Xon/Xoff". Baud: 2400.
  • Test the setup. If everything is correct, you should be able to type a capital 'Y' (that's <Shift+Y>) and the terminal should display "SM": the UPS is now in Smart Mode. Occasionally, I've had to type 'Y' twice to get a response.

    As a double-check, type a capital 'A'. Otherwise known as <Shift+A>. The UPS should beep and light up all front-panel LEDs for a couple of seconds. The terminal may display "OK".
  • Enter PROG mode by typing "1" followed by "1" again after two seconds. IF you pulled the SmartSlot card(s) out, and IF you got the timing of the "1"s right, the terminal will display "PROG". If not, try "Y" + "1" + "1" again, using different pauses. The "1" (pause) "1" is the sensitive part.

    If you made it this far, the hard part is over.
  • Enter "Battery Gain Adjust" mode. Now that the UPS is in PROG mode, capital "B" (<Shift+B>) will display a voltage (for the SUA1000XL; apparently, it shows you the Battery Gain Constant for Jacob's UPS). I consider it a reference only and near-useless. I ignore it and use the voltmeter exclusively.
    Jacob Joseph wrote:B: Battery voltage gain.
    0=maximum gain, FF=minimum gain.
    Adjust with the batteries fully charged, and an accurate voltmeter connected.
    Factory setting was "E9" on my SUA1500, and "E6" gives me the desired 27.30V battery voltage. . . .
    I agree that the battery pack must be fully-charged and a good voltmeter attached to perform any changes. Otherwise, you're going to spend a lot of time wondering why the voltage isn't changing the way you think it should.

    Keep these Adjust Battery Gain points in mind as you change this:
    • Pressing 'B' (<Shift+B>) will display a voltage. It also puts the unit in "Battery Gain Adjust" mode (my terminology). It's very easy to have it drop out of this mode!
    • In this mode, only the upper row '+' and '-' keys apply. If you press any other key, it will drop out of Battery Gain Adjust mode.
    • Pressing '+' will raise the Battery Gain constant one notch, and lower the float voltage.
    • Pressing '-' will lower the Battery Gain constant one notch, and raise the float voltage.
    • Each keypress changes the float voltage ~0.10v.
  • Adjust Battery Gain.
    With the terminal displaying your supposed battery voltage (Adjust Battery Gain mode), take note of your voltmeter's reading, then press a '+' (to lower voltage) or '-' (to raise it). All changes are immediate. The terminal should now display a two-character Gain Constant, in the range of 00 to FF, your new Battery Gain Constant. You won't know your old constant, it never showed it to you (for this model, anyway; apparently, it does show you the constant for Jacob's UPS). To determine (and record, if you wish) the old constant that you just changed, press the complementary adjust key ('+' or '-') and your old (previous) constant value will be displayed. You just moved one step away, then one step back.

    Watch the voltmeter. Wait for the new voltage to stabilize. This can be anywhere from a few seconds (for my FLAs, <10) to a couple of minutes. The battery voltage will change about one-tenth of a volt. As long as you only press '+' or '-', you can adjust up & down forever. The UPS will remain in Adjust Battery Gain mode.

    Chances are, though, that you'll eventually forget to hold down <Shift> to get the '+' key, and it will display "NO" and drop out of Adjust Battery Gain mode. To continue adjusting, re-enter the mode by pressing 'B' again. You'll be picking up where you left off.
  • End the session using 'R' (<Shift+R>). The terminal will show "BYE". You can close the terminal, disconnect the cable, etc.: you're finished. All changes are persistent.



Information on float voltage
According to Wikipedia:
Continuous-preservation (float) charging:
  • 13.4 V for gelled electrolyte
  • 13.5 V for AGM (absorbed glass mat)
  • 13.9 V for flooded cells
  • All voltages are at 20 °C (68 °F), and must be adjusted −0.0235V/°C for temperature changes.
  • Precise float voltage (±0.05 V) is critical to longevity; insufficient voltage (causes sulfation) which is almost as detrimental as excess
  • Float voltage recommendations vary, according to the manufacturer's recommendation.
My SUA1000XL has been charging to 27.66v for a 24v nominal system. This is consistent with 2.30v per cell (2.3v * 12 cells = 27.6v) for my Costco Flooded Lead Acid type batteries, and the batteries would probably be just fine if I left this charge float voltage alone. As long as the float voltage remains under the gassing voltage, the FLA batteries are fine (setting aside periodic equalization). For a 25°C/77°F temperature, that works out to

2.25 to 2.30 per cell =
13.5 to 13.8 per battery (27-27.6v for the pack)

2.39 is the gassing voltage at that temperature: 28.7v for the pack, the voltage to stay under.

However, this unit originally ships with AGM VRLA batteries, mounted inside the unit and running about 85°F+. AGM & esp. gel batteries prefer cooler temperatures, and while AGM can handle slightly higher charge voltage, gel batteries absolutely can't.

Which helps to explain why so many UPS batteries don't even make it to 3 years.

I was able to change my SUA1000XL (with external Costco FLA batteries) float voltage from a Battery Gain Constant of (unknown) and 27.67v, to constant E7 and 27.45v .

I was able to change my SUA1000 (with internal AGM VRLA batteries) float voltage from a Battery Gain Constant of (E2) and 27.77v, to constant EA and 26.92v .

(click on any image for larger)
Image
Image
Image
CSB HR 1251W F2FR wrote:Constant voltage charge, voltage regulation (20°C)
Standby use: 13.5 - 13.8v
Cycle use: 14.4 - 15.0v
Initial current: 5.1a MAX.
Image Image Image
Last edited by asavage 13 years ago, edited 3 times in total.
Regards,
Al S.

1982 Maxima diesel wagon, 2nd & 4th owner, 165k miles, rusty & burgundy/grey. Purchased 1996, SOLD 16Feb10
1983 Maxima diesel wagon, 199k miles, rusty, light yellow/light brown. SOLD 14Jul07
1981 720 SD22 (scrapped 04Sep07)
1983 Sentra CD17, 255k, bought 06Jul08, gave it away 22Jun10.
HKPolice
Posts: 4
Joined: 13 years ago

#2

Post by HKPolice »

Thank you so much for this post. I found out that one of my Smart-UPS 1500 (IBM rebranded) was charging at 27.9v! and the other was at 27.4v. I've adjusted one of them to 27.1v with genuine APC batteries and the other will be adjusted soon.

Is ~27.1v ideal for genuine APC batteries made by CSB?

Thanks!
User avatar
asavage
Site Admin
Posts: 5482
Joined: 21 years ago
Location: Oak Harbor, Wash.
Has thanked: 6 times
Been thanked: 10 times
Contact:

#3

Post by asavage »

I would think so.

CSB says: Standby use: 13.5 - 13.8v

That's 27.0 to 27.6v @ 20°C

I'm running mine at just under 27v (26.9) which is possibly too low.
Regards,
Al S.

1982 Maxima diesel wagon, 2nd & 4th owner, 165k miles, rusty & burgundy/grey. Purchased 1996, SOLD 16Feb10
1983 Maxima diesel wagon, 199k miles, rusty, light yellow/light brown. SOLD 14Jul07
1981 720 SD22 (scrapped 04Sep07)
1983 Sentra CD17, 255k, bought 06Jul08, gave it away 22Jun10.
HKPolice
Posts: 4
Joined: 13 years ago

#4

Post by HKPolice »

Do you know if it's possible to adjust the fan settings in PROG mode? Both of my IBM branded 1500 units are old so the fans don't turn on until the power goes out or running with over 75% load. I recently purchased a Dell branded SUA1500 (DLA1500) and the fan is constantly on, even when unplugged from the wall.

I did some googling and apparently all units manufactured after ~2007 are like this. The fan is supposed to spin constantly at a "low" speed, then speed up when running on batteries. Problem is that even on "low" speed, it's way too loud for home use.
User avatar
asavage
Site Admin
Posts: 5482
Joined: 21 years ago
Location: Oak Harbor, Wash.
Has thanked: 6 times
Been thanked: 10 times
Contact:

#5

Post by asavage »

I've heard of the fan problem before; fortunately, both of mine are old enough that the fan stays off until the power is out, and I really like that!

If you hear of a way to turn off the fan on the later ones, I want to know! It's not a current problem, but if I acquire a newer one . . .
Regards,
Al S.

1982 Maxima diesel wagon, 2nd & 4th owner, 165k miles, rusty & burgundy/grey. Purchased 1996, SOLD 16Feb10
1983 Maxima diesel wagon, 199k miles, rusty, light yellow/light brown. SOLD 14Jul07
1981 720 SD22 (scrapped 04Sep07)
1983 Sentra CD17, 255k, bought 06Jul08, gave it away 22Jun10.
HKPolice
Posts: 4
Joined: 13 years ago

#6

Post by HKPolice »

I took apart my UPS today to clean out the dust inside (spring cleaning) and realized that the float voltage is actually temperature sensitive. When it started out cold around ~27C it was charging at 27.3V and after a while it got up to ~31C, dropping the voltage to 27.1-27.2V. All measured with DMM and the temperature reading was from PowerChute.

I run my battery externally to keep the UPS and battery cooler so this doesn't really benefit me but it's an interesting hidden feature.
User avatar
asavage
Site Admin
Posts: 5482
Joined: 21 years ago
Location: Oak Harbor, Wash.
Has thanked: 6 times
Been thanked: 10 times
Contact:

#7

Post by asavage »

Temperature compensation for charging voltage has been around for a long time. I didn't think to mention what the temp was when I was adjusting mine. I think the CSB spec voltages were at room temp.

I run one of mine with a stock-style CSB inside (the SUA1000), and for another that has the external battery connector (SUA1000XL) I bought the mating connector from Grainger* and a bit of 10ga wire from Home Depot, and have it running on a pair of Costco (Johnson Controls) deep-cycle marine batteries in a plastic tub.

In the past, before I lowered the float voltage, I'd have to top off the batteries' water every few months, but now it does not seem to use any water.

Image Image Image


* I think the connector I purchased was an Anderson Power Products 6319 SB50, a 50A (nominal) rated unit that can accept 6 ga wire and is less than $5 from Mouser or Allied, though it's $9 at Grainger, but Grainger is my 7-Eleven and they had it in stock, so I didn't order it, I just paid the premium. I needed only the one.

Car show vendors often stock these type of connectors, too.

[May2022]
The pics above show batteries manufacturing dates of 2010. I replaced those two Kirkland batteries in 2016 (six years), and again today (six years). I think they were still operating OK in 2016 when I replaced them, but yesterday I got a red LED on the front of the SUA1000XL, "Replace Battery", and when I checked the web interface via the installed optional AP9617 Network Management card, it said, "The battery is not installed properly" followed a while later by "The battery is now installed", and eventually "Replacement Battery Needed".


APC SUA1000XL &quot;The battery is not installed properly&quot;
APC SUA1000XL "The battery is not installed properly"
SUA1000XL_10b.png (223.52 KiB) Viewed 4701963 times
APC SUA1000XL &quot;The battery is not installed properly&quot;
APC SUA1000XL "The battery is not installed properly"
SUA1000XL_11b.png (150.81 KiB) Viewed 4701963 times

APC SUA1000XL "The battery is not installed properly"


Sure enough, when I used my Schumacher BT-175 battery tester, they showed really quite bad, both of them but one quite a bit worse than the other, and they would not charge. Off to Costco, installed two new batteries, let it charge for 30 minutes, then triggered a Self-Test, and fifteen seconds later, the red LED went out and all is well.

APC SUA1000XL: &quot;No alarms present&quot; after batteries replaced and Self-Test run (tests under load).
APC SUA1000XL: "No alarms present" after batteries replaced and Self-Test run (tests under load).
SUA1000XL_13b.png (145.24 KiB) Viewed 4701963 times

Don't forget to reset the "Last Battery Replacement" date, or you may find the UPS alarming unexpectedly when it thinks the batter(ies) are EOL.


APC SUA1000XL: Reset the &quot;last battery replacement&quot; date.
APC SUA1000XL: Reset the "last battery replacement" date.
SUA1000XL_12b.png (121.32 KiB) Viewed 4701963 times

Current setup. At some point, I scrapped another huge UPS project and salvaged this nice jumper cable and terminals, so although 10 AWG wire would be more than sufficient for this UPS' load, I put this jumper here anyway.

APC SUA1000XL external batteries, May2022.
APC SUA1000XL external batteries, May2022.
SUA1000XL_09b.jpg (2.12 MiB) Viewed 4701963 times
Last edited by asavage 12 years ago, edited 1 time in total.
Regards,
Al S.

1982 Maxima diesel wagon, 2nd & 4th owner, 165k miles, rusty & burgundy/grey. Purchased 1996, SOLD 16Feb10
1983 Maxima diesel wagon, 199k miles, rusty, light yellow/light brown. SOLD 14Jul07
1981 720 SD22 (scrapped 04Sep07)
1983 Sentra CD17, 255k, bought 06Jul08, gave it away 22Jun10.
HKPolice
Posts: 4
Joined: 13 years ago

#8

Post by HKPolice »

I picked up a SUA2200 today and as expected, the float voltage was too high: 55.4v so I followed this procedure but the actual DMM voltage was not responding even though everything looked normal in Hyperterminal.

I fixed it by running APC Fix: http://www.apc-fix.com/ with Auto batt calibration checked.

Once this prog connected to the UPS, the voltage I set in HyperTerminal took effect. Running the prog again would revert the voltage back to 55.4v, requiring another connect to lower the voltages again. It's as if the UPS has 2 "modes", one where the voltage can't be adjusted and another where it can.

I have a feeling some of the UPSes that didn't respond to adjustment might just need to run the APC fix prog.
User avatar
asavage
Site Admin
Posts: 5482
Joined: 21 years ago
Location: Oak Harbor, Wash.
Has thanked: 6 times
Been thanked: 10 times
Contact:

#9

Post by asavage »

Good info, Thanks for posting it.
Regards,
Al S.

1982 Maxima diesel wagon, 2nd & 4th owner, 165k miles, rusty & burgundy/grey. Purchased 1996, SOLD 16Feb10
1983 Maxima diesel wagon, 199k miles, rusty, light yellow/light brown. SOLD 14Jul07
1981 720 SD22 (scrapped 04Sep07)
1983 Sentra CD17, 255k, bought 06Jul08, gave it away 22Jun10.
drescherjm
Posts: 1
Joined: 12 years ago

Re: Adusting battery float voltage on APC Smart-UPS SUA1000/

#10

Post by drescherjm »

Hopefully this thread revival is okay..

Anyways I have a Smart SUA1400 model that allows me to change the float voltage in the PROG mode everything appears correctly but when measuring the voltage with a DVM it is still 27.8V instead of the 26.9V I set it to even though when I query the UPS it does say the battery voltage is 26.9V I guess I will have to try APCFIX on a windows box.
User avatar
asavage
Site Admin
Posts: 5482
Joined: 21 years ago
Location: Oak Harbor, Wash.
Has thanked: 6 times
Been thanked: 10 times
Contact:

APC interface cables

#11

Post by asavage »

So many to choose from.

APC Smart UPS interface cables
APC Smart UPS interface cables
APC_Smart_UPS_interface_Cables_01b.png (166.01 KiB) Viewed 4707204 times

For the search engines . . .

Smart-UPS cables chart
  • SMX, SMT, SMC*, SRT, SURTD**
    • 940-0117B or 940-0273A (USB)
    • 940-0625A or 940-1525A (smart signaling serial)
    • 940-0128D (simple signaling serial)
  • SmartConnect SMT, SMTL, and SMC*
    • 940-0504 (USB)
    • 940-0625A or 940-1525A (smart signaling serial) (DB9F<->RJ50M)
    • 940-0128D (simple signaling serial)
  • SUA, SU, Other Smart-UPS
    • 940-0024 (smart signaling serial)
  • Any USB-compatible Smart-UPS
    • Any standard USB cable
NOTES:
* SMC model UPS do not ship with serial communications cable. SMC model UPS ship with USB cable only.

** SURTD model UPS devices and SRC2KUXI, SRC3KUXI, SRC3KUXIX709 devices must use the 940-0128D simple signaling cable.
Regards,
Al S.

1982 Maxima diesel wagon, 2nd & 4th owner, 165k miles, rusty & burgundy/grey. Purchased 1996, SOLD 16Feb10
1983 Maxima diesel wagon, 199k miles, rusty, light yellow/light brown. SOLD 14Jul07
1981 720 SD22 (scrapped 04Sep07)
1983 Sentra CD17, 255k, bought 06Jul08, gave it away 22Jun10.
User avatar
asavage
Site Admin
Posts: 5482
Joined: 21 years ago
Location: Oak Harbor, Wash.
Has thanked: 6 times
Been thanked: 10 times
Contact:

Silencing the alarm without Powerchute

#12

Post by asavage »

I just had to configure a SUA1500X93 (Shipboard/Marine version) to disable the audible alarm and set the battery date for new batteries, and over the years I'd forgotten how (without using APC Powerchute).

This model of SUA has both a DB9 Serial interface and a Type B USB interface. While setting the Battery Gain Constant requires a terminal program and one of the special serial cables, setting the alarm off requires the USB interface, so a Type B USB cable (Type B on the UPS end; whatever flavor of USB your PC requires on the other end).

Using Ubuntu 20.04

Install apcupsd:

Code: Select all

sudo apt install apcupsd
This starts & sets the monitoring/control service apcspsd, which we'll need to disable later.

Plug the USB cable into the PC and the UPS, then check to see if it's been spotted by Ubuntu:

Code: Select all

user@host:~$ lsusb
Bus 003 Device 013: ID 051d:0002 American Power Conversion Uninterruptible Power Supply
Edit /etc/apcupsd/apcupsd.conf

Code: Select all

/etc/apcupsd/apcupsd.conf

and make sure the following lines are set thus:

Code: Select all

#UPSCABLE smart
UPSCABLE usb

#UPSTYPE apcsmart
UPSTYPE usb

#DEVICE /dev/ttyS0
DEVICE
DEVICE needs to have nothing after it. For me, the defaults were fine except the DEVICE setting.

Stop the apcupsd service. If it isn't stopped, apctest won't run:

Code: Select all

sudo systemctl stop apcupsd
Run apctest and configure the Battery Date and Alarm settings. It presents a menu which requires no explanation. All settings are persistent.

---

If desired, remove the utility from the PC:

Code: Select all

sudo apt remove apcupsd
Refs.:
https://newspaint.wordpress.com/2016/07 ... ntu-14-04/
https://askubuntu.com/questions/1326402 ... accessible
Regards,
Al S.

1982 Maxima diesel wagon, 2nd & 4th owner, 165k miles, rusty & burgundy/grey. Purchased 1996, SOLD 16Feb10
1983 Maxima diesel wagon, 199k miles, rusty, light yellow/light brown. SOLD 14Jul07
1981 720 SD22 (scrapped 04Sep07)
1983 Sentra CD17, 255k, bought 06Jul08, gave it away 22Jun10.
User avatar
asavage
Site Admin
Posts: 5482
Joined: 21 years ago
Location: Oak Harbor, Wash.
Has thanked: 6 times
Been thanked: 10 times
Contact:

RBC7 Fuses

#13

Post by asavage »

If you convert an APC UPS that uses a RBC6 (Replacement Battery Cartridge 6) battery set, which uses a blade fuse and leads with 1/4" Faston female terminals, to use an RBC7, which is the same footprint but taller and higher capacity, and for which APC uses an Anderson connector that's bolted to battery tabs rather than Faston, you need to obtain the intra-pack 100A fuse. Options include:

Bussmann FLD-100
https://www.amazon.com/Bussmann-FLD-100 ... B000CF7CXG
Fuse_Bussmann_FLD-100_01b.png
Fuse_Bussmann_FLD-100_01b.png (398.05 KiB) Viewed 84621 times
Littelfuse Fuse Pal 283
https://shop.advanceautoparts.com/p/lit ... 11510130-P
Fuse_Littelfuse_Pal_283.png
Fuse_Littelfuse_Pal_283.png (340.7 KiB) Viewed 84621 times
Automotive Authority
https://www.amazon.com/Bent-Terminal-Re ... 0CWSBX43T/
Fuse_A.A.png
Fuse_A.A.png (399.46 KiB) Viewed 84621 times
Regards,
Al S.

1982 Maxima diesel wagon, 2nd & 4th owner, 165k miles, rusty & burgundy/grey. Purchased 1996, SOLD 16Feb10
1983 Maxima diesel wagon, 199k miles, rusty, light yellow/light brown. SOLD 14Jul07
1981 720 SD22 (scrapped 04Sep07)
1983 Sentra CD17, 255k, bought 06Jul08, gave it away 22Jun10.
Post Reply

Who is online

Users browsing this forum: No registered users and 18 guests